Hello, I have a Viessmann Vitocal 100-S, 8kw heat pump. The installation scheme is 6, with 2 heating circuits, a hydraulic switch and hot water heating. In coding level 1, I do not have the 7340 option, and cannot change the circulation pump operation. The pump is always 100% running and 50% 2minutes the compressor goes off. What does the "TEST PUMP" at the circulation pump mean? I am sending you pictures of the pump and installation. Best regards.
https://imgur.com/4bxffAU
https://imgur.com/mXlOGD1

https://imgur.com/0bdZz3D
38 ANTWORTEN 38

Hello Milos,

why is the compressor going? Because the setpoint was reached or because of an error message? The term "test pump" is a Grundfoss name. Built-in is a normal speed-controlled high-efficiency pump.

Best regards ° fl

Thank you for your quick response. Because the set value is reached. What is confusing is that the circulating pump is constantly operating at 100%, has no modulation based on hysterize. One of the problems that occurs when the compressor works for oil recovery, during room heating, normally the compressor increases the power during oil recovery to 75% of operation, then the starting and return T ° increases, the control registers that the heat requirement has been reached, is it the return T ° reaches the switch off point and then the circulation pump is shut down and the oil return is not yet complete and the compressor is still running, there is an increase in T ° in the exchanger as well as pressure and a high pressure error occurs. Can any parameter be changed so that the circulation pump does not shut down when the oil is returned to the compressor? Another problem that occurs to me is when the DHW is heated, the circulation pump is too fast and if the exchanger in the boiler is 4m², this does not occur in normal T °, ​​the circulation pump is running at maximum speed constantly, should it not modulate its power at based on the difference in T °? Best regards

The control is based on the flow temperature and not on the return temperature. This is the case with all modulating heat pumps. The hysteresis for switching the heat pump on and off is taken into account. At 7340, you can access the expert level. There you get over the combination "OK" + "bent arrow". The associated password is 344 254 1331. Note that equipment damage can occur due to incorrect settings in the expert level.

Best regards ° fl

I understand the risk, but also at coding level 2, expert, I do not have cod 7340, it has 7341 (50 is set) which is a parameter for the minimum power of the circulation pump, 7342 (100 is set) for maximum power and 7432 (100 is set) for adjustment pumps with pump on the secondary side.

Can you tell me what the code is for adjusting the speed or power of the circulation pump when heating DHW?
Pictured are the serial numbers of the heat pump,if necessary to determine which control unit is installed.

https://imgur.com/sXUf9rO

https://imgur.com/5YjTFgk

Best regards
Milos

The parameters that govern the speed adjustment of the secondary pump during DHW are 6020, 6021, 6022 and 6023. However, this requires that parameter 7340 is set to 4. Since you cannot access it, you have to check whether it works or not.

6020: 3 - Speed-controlled operation, control via PWM
6021 - Min. Output storage tank charging pump
6022 - Max. Output storage tank charging pump
6023 - Nominal output of the primary store pump

Best regards ° fl

The video shows the codes in the expert coding mode, which I have. No cods 7340 and 6020.

https://youtu.be/sdFdrSUubO0
https://youtu.be/12sx8t6k1Bw

The software version is probably too old, which is why the parameter has not yet been displayed there.

Best regards °fl

Is there a possibility to upgrade the software?
Does the plugin code depend on the software version or does it depend on the version of the electronic board?

Software version
Code plug

https://imgur.com/dIn4ytg

This is very frustrating for me, I buy a new device, and I get old software ... I feel disappointed.

Changing the parameters 6021,6022 and 6023 has no effect on the circulation pump. Also parameters 7341 and 7342 have no effect. Only the 7343 has an effect, it only limits the maximum power of the circulation pump and that only for heating, DHW heating has no effect and the circulation pump runs 100% all the time.

Can you tell me which country you are from or in which country the device is installed?

Best regards °fl

Serbia

I recommend that you contact my colleagues in Serbia about this.

https://www.viessmann.rs/sr/kontakt/predstavnistvo-u-srbiji.html

Best regards °fl

I contacted Viessmann in my country.
I'm expecting an answer.
Can you tell me, what is the solution to my problem?

Best regards
Miloš

The solution ist a software update.

Best regards °fl

I have not yet received a response from Viessmann Serbia.
The software update requires replacement of some components or not.

The decision for this is made by the colleagues from Serbia.

Best regards °fl

No feedback yet from Viessmann Serbia and the installation company.
Does the code plug affect the software version?

Mr. Flo, Does the Vitocal 100-s heat pump modulate the outdoor unit's fan operation or does it operate at a constant speed?
87% of my work is constantly done, 1/16 notification is frequent.
So I'm interested in whether it is normal operation or a consequence of an older version of the software, as with a circulation pump which is.

Best regards
Milos

Hello Milos,

did you try to call my colleagues there?

The fan speed is speed-controlled and is adjusted to the degree of modulation of the compressor.

Best regards °fl

I contacted 13.12.2019 via email, Viessmann.rs and the company https://www.loren-line.com/ performed the installation, as recommended by Viessmann.
I also posted a link to this forum and this thread.
Still, I have not received any response.

Please try to call the colleagues.

Best regards °fl

I was at the company www.Loren-line.com, yesterday 09.01 personally, Viessmann.rs refers to them as installers, so then they contact Viessmann.rs, I was told that they received a mail sent on 13.12.2019, I expect a reply to the end of next week. If I do not get a response, I will ask my rights through a lawyer, the device is still under warranty.

Mr.Flo, here's a video where I managed to capture the moment of shutdown due to high pressure error 07, on heating, **bleep** defrosting