Dear all,

 

I have question about energy statement. Vitronic 200 is showing only heating energy transferred to system but not energy used for heat pump.

Also SPF rates are invalid from the same reason.

 

Any help for this issue and apologies about English language.

 

Pump: Vitocal 200G 2021 17,4kW new generation.

 

With best regards

 

Matti,  Finland

9F11C144-5C5C-41BB-8AD5-8E43D07F1613.jpeg

 

 

 

5 ANTWORTEN 5

Hello Matti,

 

please check the following parameters.

 

8811: 2
8812: >1
8814: 1023
8815: 1023
8817: 1023
8818: 31
8819: 31 
881A: 31
881B: 31 

 

Some may be in the second coding level.To do this, press and hold the "OK" and "Back" buttons for approx. 4 seconds in the service level (OK and menu).  Then enter the code 344 254 1331. Important! Incorrect settings in the expert level can cause damage to the unit. 

 

Best regards
Flo

​​​​​​

Hello Flo,

 

Thank You about promp reply,

I checked my system parametres.

 

8811: 1
8812: 128
8814: 1023
8815: 768
8817: 1023
8818: 31
8819: 31 
881A: 31
881B: 31

Shall I change parametres which You send?


Thank You!

 

Matti

 

 

Yes, change the parameters 8811 and 8815 as I described. 

 

Many greetings
Flo

Hallo Flo,

 

Changed parameters but unfortunatelly no results. Any other ideas?

 

Thank You in advance.

 

With best regards

 

Matti

No, unfortunately not. Please contact the sales office responsible for you in your country.

 

Many greetings
Flo

 